    Re: Process gateway modbus | dcs

    the MODBUS protocol does not have something like quality flags known (and very useful) in energy protocols (IEC 61850, IEC 60870, DNP3). Thus, when zenon IEC850 driver losses connection to IED,...
  2. Replies
    1
    Views
    3,689

    Re: OPC-UA driver issue

    Forum is <u>not</u> the official way to make an agreement about porting of fixes to some old version.&nbsp;For&nbsp;zenon 7.50 the end of product fixes builds for customer not having SLA was already...
  3. Replies
    3
    Views
    13,064

    Re: Distrurbance record using IEC-103

    The zenon IEC870_103 (master) driver, if correctly configured, transfers the data recorded in the outstation (in an 103-slave) exactly according the guidelines of IEC 60870-5-103 protocol and...
  4. Replies
    2
    Views
    17,233

    Re: Integer value with decimal seperators

    In zenon the char for&nbsp;decimal separator is this from Windows current settings, the quantity of decimal places you can set by variable in the property 'Value calculation' - 'Decimals'.<br><br>The...
  5. Replies
    3
    Views
    13,132

    Re: Restart Runtime

    Does the runtime application crash (= ends unexpected)? or just the main screen (the biggest frame) is closed/hidden? <br><br>If it is just closed frame/screen - maybe try: call the function closing...
  6. [SOLVED] Re: Process Gateway OPC UA used to initiate IEC61850 Double Commands

    Unfortunately, there is no option to suppress the user interaction generally.

    Maybe you can create more complex sequences (including conditional cross-checks before executing switch/set-point...
  7. Replies
    2
    Views
    6,458

    Re: Reaction matrix - string not empty

    you need in rema at least two new entries (conditions), the default&nbsp;by default, the first created entry if empty (Equal=) and the second if not empty&nbsp;(Any); and consider if you need the...
  8. Replies
    1
    Views
    1,942

    Re: Device connections

    result of a small search&nbsp;on this&nbsp;forum: <a...
  9. Replies
    3
    Views
    2,363

    Re: IEC870 driver, use originator in REMA

    <span style="color: rgb(105, 105, 105);">&gt;Do you know if this feature from AKdriver will be implemented in Energy Edition in the future?</span><br>Hmm, I suppose&nbsp;the question is not to my...
  10. Re: Trouble with connecting ABB REF615 via modbus

    I suppose&nbsp;the SlaveID number&nbsp;is wrong, e.g. 0 (number zero is reserved for broadcasts). In&nbsp;the MODRTU driver&nbsp;the Slave Id (some&nbsp;device manufacturer&nbsp;use "device id" or...
  11. Replies
    3
    Views
    2,363

    Re: IEC870 driver, use originator in REMA

    I suppose in SICAM 230, in the AK-driver,&nbsp;there is/was an extra feature - the mapping of IEC60870 <em>Originator</em> to some of user status bits (M1-M8)&nbsp;of the variable value. <br><br>In...
  12. [SOLVED] Re: Connection Timeout When Remove DO Card from RTU

    <span style="color: rgb(105, 105, 105);">&gt;As you have mentioned Positive Case, does it depends on any hardware condition of RTU (e.g. Relay faulty or Healthy)?</span><br><br>Ask the manufacturer of...
  13. [SOLVED] Re: Connection Timeout When Remove DO Card from RTU

    hmm, I see I have to repeat the explanation using another words.. ok, the second try to explain:

    When the user press action button then the driver sends to RTU the Select - In Wireshark it is...
  14. [SOLVED] Re: Connection Timeout When Remove DO Card from RTU

    What driver are you using? in zenon&nbsp;all energy drivers are mapping/transferring the COT to the Runtime. IEC870, IEC850&nbsp;or DNP3?<br>Forum is not the right place to request analyzes of...
  15. Replies
    4
    Views
    641

    Re: Periodic Synchronization of PLC

    Are the modern computers performant enough to do some simple task each 5 minutes :confused:

    zenon has a function queue (help: Manual > Functions and scripts > Functions > Execution sequence during...
  16. Replies
    2
    Views
    473

    Re: Bachmann Communication Problem

    I have no experience with the Bachmann driver, but generally any TCP/IP-basing zenon driver tries to reconnect 30s after the&nbsp;previous success/failed opening of TCP socket. <br><br>So,...
  17. Replies
    2
    Views
    447

    Re: Connection error variable.

    what you write looks&nbsp;like general Communication Info variable (general but not precise, as in&nbsp;any zenon driver). <br>In iec870&nbsp;there is a special ConnectionState solution (Help...
  18. Replies
    4
    Views
    641

    Re: Periodic Synchronization of PLC

    Create T103 variable(s) and zenon function 'write set value' to this variable. In the function activate the&nbsp;option 'directly to the Hardware'. Then link the function in the module Time Control.
  19. Re: Zenon Energy Edition IEC104 driver Redundancy According Edition 2 LANGROUPS

    In zenon help you will not find copies of text of international standards.<br><br>The IEC 60870-5-104 edition 2.0 redundancy, described very simplified, demands that on all N channels (e.g. via...
  20. Re: White screen in the Runtime for the subproject

    It is hard to guess what is wrong configured.
    Are you using the GLOBAL project? I would recommend to avoid situations when the screen has frame, symbols etc, some from own, some from another...
  21. Re: Response variable value Command Processing

    hint: you can use also visibility or dynamical color settings of the&nbsp;action buttons&nbsp;to change the look of the relevant&nbsp;button (while "Auto"&nbsp;the button [Hand] looks welcoming, and...
  22. Re: Response variable value Command Processing

    see: Manual &gt; Energy Edition &gt; Command Processing &gt; Engineering in the Editor &gt; Creating a screen of the type Command Processing &gt; Substitution of additional variables in the screen<br><br>0....
  23. Replies
    1
    Views
    983

    Re: CCTV Intergration

    video stream is not an energy specific feature, thus i'm moving this thread, else you have no chance that a specialist will see it&nbsp;and could give an advice.
  24. Re: Zenon Energy Edition IEC104 driver Redundancy According Edition 2 LANGROUPS

    What you are describing it&nbsp;is <u>not</u> the IEC60870-5-104 Edition 2.0 redundancy. The standard defines the redundancy of the Data Link layer: between <u>single</u> controlling station (master,...
  25. Re: CEL does not arrange event follow timestamp automatically

    Just to clarify: some very, very long BufTm could be the reason, but only as long different *stVal[ST]&nbsp;variables are changing, not the same one&nbsp;(BufTm affects events on <u>different</u>...