  1. Re: Importing variables and Client IED name in IEC850 driver configuration wizard

    ad. "Primary: Hostname: SCADA_SERVER1, ClientLN.iedName: Client1"<br><br>you are consequently making&nbsp;typing mistake in Hostname keyword&nbsp;(and this is also probably reason of your confusion...
  2. Re: Importing variables and Client IED name in IEC850 driver configuration wizard

    Ad. no variables to import in Wizard&nbsp;<br>On screenshot with the list of RCBs in IED (left panel)&nbsp;I see that all those RCBs have <u>no</u> data sets.&nbsp;Else by each RCB name you would...
  3. Replies
    1
    Views
    252

    Re: Downgrade form 7.60 to 7.20

    In 7.60 Editor you can compile project for 7.20 Runtime.&nbsp;But then this Runtime will&nbsp;do only this&nbsp;what it can, and it can only 7.20.&nbsp;The Runtime ignores&nbsp;what it does not know.
  4. Replies
    3
    Views
    332

    Re: Disable Alarm Functions at Nighttime

    nice idea.<br><br><em>but this topic is nothing specific for energy, so i'm moving this thread.</em>
  5. Replies
    9
    Views
    546

    Re: Straton IEC 60870 104 Slave Timestamp

    even if you repeat the question the answer is still the same: <ul><li>the time the slave driver&nbsp;sends is the time&nbsp;determined&nbsp;by the computer clock. The slave driver does it...
  6. Replies
    9
    Views
    546

    Re: Straton IEC 60870 104 Slave Timestamp

    Wireshark is a sniffing program. Wikipedia?&nbsp;
  7. Replies
    9
    Views
    546

    Re: Straton IEC 60870 104 Slave Timestamp

    When variable is configured as T30, 31 etc. and you are <u>not</u> using the VSISetDate function, then by any value change the driver sends&nbsp;this value with the time stamp equal the&nbsp;current...
  8. Replies
    1
    Views
    492

    Re: Error: Too many IO variables

    check your license, menu - Help - About
  9. Replies
    4
    Views
    326

    Re: GOOSE publisher via zenon Logic

    GOOSE is not the right protocol to open/close circuit breakers from a&nbsp;SCADA system.&nbsp;GOOSE&nbsp;is a way for e.g.&nbsp;Protection devices to&nbsp;send the signal to&nbsp;trip (force...
  10. Replies
    9
    Views
    546

    Re: Straton IEC 60870 104 Slave Timestamp

    <img class="previewthumb" id="vbattach_2963" alt="" src="https://forum.copadata.com/attachment.php?attachmentid=2963&amp;stc=1" attachmentid="2963"><br><br>When you program changes the&nbsp;variable...
  11. Re: INTERN and SIMUL32 driver in Command Processing

    see zenon Help: Manual &gt; zenon Logic &gt; zenon Logic Runtime for Windows &gt; Licensing &gt; TAG handling zenon - zenon Logic<br><br>The number of the TAGs used in zenon Logic is the number of I/Os...
  12. Replies
    8
    Views
    653

    Re: Function and scripts

    your screenshots are from Editor set to use language I do not understand, so i'm not able to guess what settings you show. For publishing screenshots switch Editor to English.
    The relevant things...
  13. Replies
    8
    Views
    653

    Re: Function and scripts

    when you link with a button not a function but a script, then in the background, the zenon Editor automatically creates a new, additional&nbsp;function calling this script an links...
  14. Re: command processing for setpoint values, responsvalue question.

    All zenon drivers, so also IEC870, write to PLC&nbsp;when the zenon Runtime pokes (transfers) the&nbsp;new proposed variable value to the driver. In zenon variables have&nbsp;the updated&nbsp;value...
  15. Replies
    2
    Views
    358

    Re: Enable report control blocks

    <span style="color: rgb(105, 105, 105);">&gt;But I was not able to disable or enable RCBs. Is this a possibility in zenon? </span><br><br>At the start of zenon Runtime,&nbsp;the&nbsp;IEC850 driver...
  16. Replies
    2
    Views
    233

    [SOLVED] Re: Get/Set resource label with zenon logic

    NO.<br><br>If I right remember you can only get (but for sure not&nbsp;set) the name of variable as&nbsp;STRING (via access to it as&nbsp;"symbol"). Or to be more precise - the string which is the...
  17. Re: Reading RDA Array(Real Data Type) from Beckhoff Twincat NG Driver

    Have you tried to rebuild the TPY-file and re-import the variables?
  18. Re: Application SysSrvCE. EXE encountered a serious error

    Sicam 230 is product of Siemens, not COPA-DATA. It bases partially on zenon but for very old version 6.22 we are not providing support anymore. Try by Siemens support.&nbsp;
  19. Re: command processing for setpoint values, responsvalue question.

    I understand your point, but the command screen does not have such feature. You can display in screen the value of RV but the editable value of the command is another field - this with value of...
  20. Re: INTERN and SIMUL32 driver in Command Processing

    <span style="color: rgb(105, 105, 105);">&gt;I read older post in the forum and it seems they recommend to use&nbsp; INTERN driver instead of SIMUL32 driver.</span><br><br>I'm not finding such forum...
  21. Replies
    1
    Views
    450

    Re: Statistics in Process Gateway

    The window is general - common for all protocols supported by zenon Process Gateway. I suppose in Modbus this Information is not available. <br>&nbsp;<em><br>As this is not an Energy-specific topic,...
  22. Replies
    5
    Views
    495

    Re: Distributed Engineering License doubts

    <em>as this is not an Energy specific question, i'm moving it to&nbsp;another forum node.<br><br></em>The distributed engineering does not need to be extra licensed, but of course it&nbsp;demands...
  23. Thread: Alarm list

    by ursulak
    Replies
    2
    Views
    1,956

    Re: Alarm list

    The&nbsp;Alarm List cannot be exceeded. Only&nbsp;the hard drive space in the PC where your zenon Runtime&nbsp;stores historical alarms can be exceeded.&nbsp;In zenon&nbsp;you can check the HDD usage...
  24. Replies
    1
    Views
    611

    Re: Driver creation

    Generally - do like you want.&nbsp;It has no significant impact.<br><br>Only if&nbsp;each device delivers much data (thousands of variables&nbsp;and values changing frequently)&nbsp;and/or you have a...
  25. Replies
    3
    Views
    481

    Re: Bar display - Zenon logic

    Check if the variable in zenon has correctly configured as well signal as measuring ranges. Maybe (by data type change) you mistakenly "configured" the linear value adjustment. <br>And by 'Bar...